Hi all, I am looking for a sanity check on a water supply calculation for water main with significant elevation delta.
We ran a hydrant test on a dead-end run for a new development that is fed from a city main at the top of a hill. The two furthest hydrants were tested, the flow hydrant at the dead-end and pressure hydrant mid-way down the hill. City Main = EL 500 Pressure Hydrant = EL 450 Flow Hydrant = EL 400 Proposed FFE = EL 425 The Freeman Flow equation bases hydrant flow on pitot pressure (PSIG) which is relative to the hydrant elevation. To calculate R20 (ie 20PSIG) at that hydrant elevation we use a ratio of PSIG values from the pressure hydrant normalized to 1.85 power multiplied by the hydrant flow rate from Freeman equation. It is at this point that I begin second-guessing: the ratio that is being used does not take into account the elevation delta as it is PSIG. I have calculated the HGLs for the three pressures based on converting PSIG at its respective elevation. My initial thought is that the pressure hydrant PSIGs (based on EL 450) should be converted to PSIGs at the flow hydrant (ie based on EL 400) by means of HGL - Hydrant Elevation and then using those "adjusted" PSIG static/residual values as the scaling terms for R20 at the flow hydrant. Then to get a theoretical R20 for a future hydrant at FFE I would repeat the same process, this time normalizing pressure hydrant static/residual HGLs to FFE elevation, holding the Freeman Flow value constant, and using a "new" R20 = 20PSIG at FFE. On the face I get reasonable values, but would like to get feedback from the group. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
2 Comments
Dan Wilder
11/5/2024 09:27:39 am
So the effective point of the fire hydrant test is at the connection of the Static/Residual hydrant to the flowing main. I am unclear as to is the main sits at EL 500 and there are smaller laterals to the hydrants at EL 450 or if this is just one long downhill path.
Reply
Eric R
11/5/2024 10:25:54 am
If your goal is to determine available water supply at the service line connection to a new building with the finished floor elevation of 425' then I feel that you are not accounting for pipe size and run-length in your calculation.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop Oct '26 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
November 2026
PE PREP SERIES |
RSS Feed