|
Can I add a fire pump to my combination Manual wet standpipe and sprinkler system and still use a manual wet standpipe?
Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
5 Comments
9/30/2019 10:23:56 am
Yes, your fire pump is sized only for the greatest sprinkler demand. Be careful that your pipe sizing through the pump and around the bypass meet the larger demand. A calculation should really be performed on the manual wet standpipes using the local responding fire departments standard pressure from the pumper truck (usually 150 psi from my experience, more if the building is taller). This is how you should determine your standpipe sizing, or in whatever method is approved by the AHJ. For example, if your sprinkler demand is fairly low in GPM, you might be able to get by with 4" or less of suction, discharge, and bypass piping, but that doesn't mean that 4" is enough for the manual wet standpipe demand. Hope that helps.
Reply
9/30/2019 04:10:26 pm
Unless I"m misunderstanding you, I must respectfully disagree with this response. In no situation (that I am aware of) would your FDC be upstream of your fire pump suction. Therefore, your fire pump pipe size and bypass size would have no affect on a manual standpipe downstream of the fire pump. You would just need to insure that the FDC, which should be connected downstream of your fire pump check valve, was at minimum, the same size as your Manual Standpipe.
Reply
Casey Milhorn
9/30/2019 05:07:06 pm
Yeah, I shouldn't have said the suction sizing. I'm talking more if the FDC is tied into the bypass piping. The bypass piping, and anything downstream of the FDC should be sized with the manual wet standpipe in mind. Thanks for the correction.
Pari
9/30/2019 01:20:52 pm
Yes, you can do that as long as the system is not serving high rise building.
Reply
Colin Lusher
9/30/2019 03:59:40 pm
This depends on the building height and your AHJ. If your building is classified as a high rise, then NFPA 14 requires an Automatic standpipe system, however, when retrofitting an existing non-sprinklered high rise building with an automatic sprinkler system, many jurisdictions will allow the standpipe system to remain "manual". In this situation for example, in my jurisdiction, the AHJ allows us to convert the existing dry standpipe system to a manual wet system; the old dry standpipes service the new sprinkler system, but we size the pump only for the fire sprinkler system, and the standpipe demand must be met by the fire department at the FDC.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop Sept '26 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
October 2026
PE PREP SERIES |
RSS Feed
