When doing Calculations for a building that has a fire pump that is fed by an above-ground water tank, what do I use for available supply?
The fire Pump is 75 psi at 1,500 gpm. City water refills the water tank. City water is 104 psi static, 81 residual at 1,453 gpm flow. Do I factor in the tank by figuring the pressure created by elevation, or do I bypass the tank and use the city pressure in combination with the fire pump? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
18 Comments
Pete H
12/12/2024 07:05:16 am
As the water goes through the tank before the pump, I'd factor in the tank and the elevation that comes with it. Even consider noting that you did that on the drawing via a hydraulic note.
Reply
Dan Wilder
12/12/2024 07:25:48 am
Unless you're using a pressure tank, the static head at high and low points on the tank would be your supply.
Reply
JI
12/12/2024 08:14:21 am
Use the worst case scenario for hydraulic calculations (fire pump only), and the best case scenario (fire pump + head from tank) for potential pressure regulating devices.
Reply
Mike Morey
12/12/2024 08:38:44 am
This is, imho, the correct way to do it. Tank minimum water level a the end of the fire event head pressure minus friction loss if applicable is your supply. When you've used up your required duration x flow the tank won't be full, so your calc needs to account for that. But you need to factor in high water plus churn for any maximum pressure limited devices.
Reply
Casey Milhorn
12/12/2024 08:53:18 am
Mike is definitely correct. To complicate things even more, if your city main has a bypass line that is normally open (which is not typical), you would also have to do a churn calc with city static pressure and make sure all downstream items are rated for that pressure, or have a pressured reduction strategy in place (which then typically makes the tank only calc not work).
Jonathan Lo
12/12/2024 10:48:32 am
I like this explanation, and the logic behind it.
Reply
Glenn Berger
12/12/2024 08:42:26 am
Unless you have some unique piping arrangement - The water source for the sprinkler system is the water tank and the fire pump.
Reply
Anthony
12/12/2024 08:52:50 am
Use the lowest level of the tank that will supply the fire pump as that is how the tank was sized. Probably a 60 min duration X the demand get you your tank size given the flow requirements of 1500gpm.
Reply
Jack G
12/12/2024 09:01:27 am
I will assume this is not a pressure tank.
Reply
Jose Figueroa
12/12/2024 09:09:00 am
1) If the public supply is used to fill the tank, it should not be included in the calculations for the system.
Reply
Jesse
12/12/2024 10:03:36 am
Unless the city water adds material value to the pressure, don't include it.
Reply
Jose Figueroa
12/12/2024 02:35:05 pm
I find it quite surprising that many readers of this blog perceive the decision-making process in this context as akin to cherry-picking. It seems there might be an oversight of the crucial engineering principles involved. The best response to the questions raised is often “it depends” and “we require further engineering details and variables to provide a thorough answer.” It may be beneficial for MeyerFire’s reputation to consider implementing some moderation in discussions.
Reply
Joe Meyer
12/12/2024 03:08:12 pm
Jose, please elaborate.
Reply
Anthony
12/12/2024 03:33:38 pm
Well said Joe!
Jose Figueroa
12/12/2024 04:05:42 pm
Dear John and everyone,
Reply
Jose Figueroa
12/12/2024 06:24:00 pm
Question 1: When doing Calculations for a building that has a fire pump that is fed by an above-ground water tank, what do I use for available supply?
Reply
The water distribution system is providing 1,453 gpm @ 81 PSI residual. At 20 PSI it should be producing 2,925 gpm. At that rate of fill there should be sufficient water for the pump and any hose lines used by the Fire Department baring master streams or crash vehicle resupply.
Reply
Anonymous
1/16/2025 08:30:00 am
In terms of the code and design with a static tank at grade the pressure from the city or the static pressure from the tank should not be added to the fire pump calculation.