There is a seemingly willful gap in information in scoping code (IBC) for small group R structures: those on the threshold of IRC/IBC: I am working on an existing 4 unit building where we do not have verified assembly information so the construction is assumed to be V-B.
The owner would like to renovate the existing basement, which is ~50% above grade, into an apartment with a new exterior exit. Three of the units share a common interior exit stairway & the upper ones are served by a fire escape. The 4th unit is built like a townhouse on the rear of the building and does not share any exit components. If an existing 4-unit residential building (currently not sprinkler protected) adds a 5th unit in the basement — and that unit does not share exit components — is there a code path that allows the project to proceed without installing sprinklers throughout the entire building? Or, a way to construct the new unit in an existing fire area in a way that does not increase risk (ie: 2-hour separation)? While the group is a trigger for requiring a system, looking at Chapter 5 as a scoping reference, the total fire area is below the threshold for a sprinkler system in group R-2 with V-B construction. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments
ChaD
3/6/2026 09:38:42 am
Yes, you will need to separate the other unit from the rest of the building by 2hr construction though. I dont have code books in front of me but there is a code path for it. Sometimes though, its just easier to sprinkle it all, leaving CPVC exposed....assuming the clientele/renters will live with that. A whole lot of side walls.
Reply
Jack G
3/6/2026 11:46:01 am
Don t know what happened but if zoned r-2 or r-3, they needed protection for 4 units, unless 2 story townhomes .
Reply
Brett
3/6/2026 01:09:57 pm
Since it's an existing building you should be looking at the existing building code. If NFPA 101 applies then look at chapter 43.
Reply
Tim
3/9/2026 02:00:20 pm
As a plan examiner, I'm not going to care which code it was built under when you're adding density to an R2. I'm going to try to get a sprinkler in that building. But, Chapter 8 of the IEBC has a workaround. I might still ask for upgraded smoke detectors upstairs.