Access Required for Concealed Space Sprinklers?

10/25/2021

12 Comments

 
Is an access panel or access door required for sprinklers that are installed in a concealed space?

​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments
Dan Wilder
10/25/2021 07:37:40 am

NFPA 13-19'-9.3.9.3 Sprinkler Access - Access shall be provided to all sprinklers for inspection, testing, and maintenance.
Similar to 16.1.1 for access to system valves & gauges, 16.9.3.1.1/16.9.3.4 for valves, 16.10.5.2.1 for Auxiliary Drains, etc.

Then goes to what "access" means....is an 18x18 or 24x24 panel used by the HVAC trades to get to an AHU compliance with those sections regardless of how far one would have to travel above the ceiling? Good practice would prefer additional points it but depending on height above the ceiling to the piping, ability to transverse across the ceiling, and if the access point is large enough to perform work through all come into play.

NFPA 25 is specific that inspections are to occur from the "floor level" for sprinklers. The internal inspection of piping could require access above the ceiling depending on the location if it falls into the four points identified within NFPA 25, but falls short of requiring provisions for access to these locations.

Reply
TC
10/27/2021 09:41:26 am

NFPA 13 2019- 9.3.9.3 is a subsection of 9.3.9 Duct Protection- this requirement for access panel is for Duct sprinklers.
there is no requirement in NFPA 13 for access to sprinklers in concealed spaces.

Reply
Alex
10/25/2021 07:58:56 am

Hi Anonymous,

Inspection and maintenance for sprinklers is discussed in both NFPA 13 and 25.

NFPA 13 (2016) 8.15.13.3 states that "access shall be provided to all sprinklers for inspection, testing and maintenance."

NFPA 25 (2020) 4.1.3 states that the “property owner… shall provide ready accessibility to components of water-based fire protection system that require inspection, testing, and maintenance.” Based on NFPA 25, sprinklers shall be inspected from the floor annually. Although, 5.2.1.1.3 states that sprinklers installed within concealed spaces shall not require inspection.

With that said, I do not believe you need to install access panels for concealed space sprinklers. I would love to watch you tell an architect that you want to install panels though! Architects love access panels…

Thanks,
Alex

Reply
Dave
10/25/2021 10:18:44 am

Since 8.15.13.3 (2016) is a subsection of 8.15.13, that is only for duct sprinklers. There is no requirement in NFPA 13 or 25 for access panels for concealed spaces. Although I have seen owners wish to have them provided, and I have seen military specs requiring them.

Reply
Alex
10/25/2021 01:21:04 pm

Hi Dave,

Tough oversight on my part. Thank you for pointing that out!

Alex

Jack G
10/25/2021 08:21:30 am

Back in the day, 51 years ago, architects would show access panels in hard ceilings next to where designers would place the sprinkler heads for , specifically for access, repair.
The frames would, should be turned in the direction of the branch lines.
It should be no different now.
“Aesthetics”—- architects should toss that word out of their vocabulary and replace it with “ Safety “. !

Reply
Todd Wyatt
10/25/2021 09:34:19 am

The Specifications (e.g. 083113 Access Doors and Frames) instruct the Contractor to "Verify access door locations and sizes provide required maintenance access to installed building services components." and "Install access doors and panels permitting access to service valves, traps, dampers, cleanouts, and other mechanical, electrical and conveyor control items concealed in walls and partitions, and concealed above gypsum board and plaster ceilings."

Reply
Jesse
10/25/2021 10:26:07 am

There is a lot of debate within the AHJs in my area about this.

13 states access shall be provided for inspection, testing, and maintenance. 25 states sprinklers shall be visualized from the floor.

So we typically discuss what the AHJ wants ahead of time. Most of them don't bother to look at concealed space sprinklers after the original install visual is done, although access is provided.

Reply
Dave
10/25/2021 11:33:44 am

NFPA #13:
"Access shall be provided for inspection, testing, and maintenance"

The phrase as appears in 8.9.7 falls under 8.9, which is Commercial-Type Cooking Equipment and Ventilation.

The phrase as appears in 9.3.9.3 falls under 9.3.9 which is Duct Protection.

Must always look at the root paragraph. I am not aware of this phrase referring to sprinklers in all concealed spaces.

Reply
DON BERRY
10/11/2022 01:30:33 pm

If a concealed space requires sprinklers (like a wood truss attic),is not inspected, how do you know if the fire protection for the attic meets code? NFPA 13 requires all heads to be inspected.

Reply
Brennan
7/17/2023 05:40:37 pm

You would get an inspection signed off by the ahj before they installed sheet rock on the underside of the trusses.

Reply
Jonathan
5/21/2024 12:40:39 pm

Is there a minimum size access panel for the Inspectors Test valve located within a wall/chase? I'm having difficulty finding any concrete answers.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT