|
In a highrise building with a sprinkler system designed under NFPA 13, are above-ceiling smoke detectors required?
There are limited combustible materials (wiring, steel pipe, steel ductwork) and in other areas PVC pipe. Are smoke detectors required for the above ceiling spaces? Should they be considered if not? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments
Todd Wyatt
7/10/2026 08:16:22 am
It depends ... some high-rise jurisdictions (LA, NYC, Chicago) write custom Fire Code amendments mandating that if sprinklers are omitted from any small concealed space per NFPA 13 permissions, a smoke or heat detector must be provided in its place.
Reply
Glenn Berger
7/10/2026 08:28:18 am
As Todd indicated, need to verify with applicable codes, especially those with local amendments. Based upon national codes and NFPA standards, smoke detection would not be required in your application.
Reply
Jocelyn
7/10/2026 12:29:15 pm
Assuming you are using the IBC with no amendments, the high-rise smoke detection requirements in IBC 907.2.13.1 identify the spaces where smoke detection is required. There are no requirements for total smoke detection coverage throughout the building.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop July '26 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
September 2026
PE PREP SERIES |
RSS Feed
