I have a project for which someone else did the flow test for me. At the test hydrant, I have a static of 69 psi and a residual of 64 psi at an elevation of 238'.
According to the information I was given at the flow hydrant, I have a static of 24 psi and a pitot of 25 psi at an elevation of 308'. With a coefficient of .90, they show a flow of 839 gpm. My question is - do you think it is acceptable to use a flow test showing a pitot reading higher than the static read at the same hydrant? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
19 Comments
Dan
2/14/2025 08:14:08 am
Static at the flow hydrant should be identical to static at the test hydrant minus the elevation difference. A 70 ft elevation difference would yield a pressure delta of 30.31 psi. Your static at the higher elevation should be 38.69 psi. This is possibly a typo and I would ask for clarification from the testing party, or conduct a retest.
Reply
2/14/2025 08:16:08 am
It does seem a little odd. It would depend on what they are using as the "Nozzle" to measure the flow. I would confirm with them the device using for the measurement.
Reply
Jesse
2/14/2025 08:16:13 am
Yep that's not a problem. The pitot measures or quantifies a different element of the water supply system. The static pressures measures the outward pressure the water provides while static or stationary. i.e. not moving.
Reply
Matt C
2/14/2025 08:17:36 am
Pressure and Velocity pressure aren't the same thing. If the idea of the residual number being higher bothers you then just express it in gpm rather than psi pitot. It's also easier for the layman to understand flow in gpm rather than wrap their head around two units representing two different things that look similar on paper.
Reply
Randy Kimbro
2/14/2025 08:18:20 am
I agree with Dan. Not only that, but the pitot reading should never be higher than the static reading. Since water is flowing with the pitot reading, that reading is theoretically impossible. As an AHJ, I would require a retest with us witnessing the process.
Reply
Leighton
2/14/2025 11:07:16 am
I bet the water supply has a pump that kicks on while a flow condition is happening. Or some other type of system in place.
Reply
Joe M
2/14/2025 08:21:54 am
Additional I would like to know if liquid filled gauges were use and if there were calibrated within the last year.
Reply
Glenn Berger
2/14/2025 08:25:38 am
As others have said - Static pressure and pitot pressure measurements at the same hydrant are uniquely different. No issues with using those readings.
Reply
Casey Milhorn
2/14/2025 08:37:11 am
Agree with most everyone else. Not an issue. I will add, too many people will try and use a residual pressure reading and equate that to a pitot reading. Though sometimes similar readings, it is NOT the same. Always get an actual pitot pressure to determine flow.
Reply
Franck
2/14/2025 08:47:30 am
Static and residual pressures are information related to the fire mains. They shouldn not be taken at the hydrant that is flowing.
Reply
Jose Figueroa
2/14/2025 08:49:34 am
Velocity pressure (Pitot Reading) is independent of static pressure. I cannot observe the diameter of the nozzle, and I find no issues with the test results. Thank you.
Reply
Jack G
2/14/2025 10:00:57 am
It sounds like the following might be affecting your test.
Reply
Robert Hughes
2/14/2025 10:20:46 am
The guages used are not micrometers, and are prone to vibration.
Reply
Pete H
2/14/2025 10:38:25 am
Seems fine.... any chance you can measure flow at the hydrant in GPM and see if it is in line with the Pitot reading at that static?
Reply
Dave L.
2/14/2025 10:39:03 am
I can't overstate (so I'm going to repeat it) what was mentioned above about making sure the gauges have been calibrated within the last year. Ours go in same time every year (just took mine in yesterday) and it is not unusual for one to need calibration, and last year one was found to be unrepairable. (And if I'm going to put my name on it, the report would be more presentable.)
Reply
Jerry Clark
2/14/2025 11:59:16 am
No, it is not acceptable to use a flow test where the pitot reading is higher than the static pressure at the same hydrant. This suggests an error in measurement or recording.
Reply
Ivan J. Humberson
2/17/2025 11:28:13 am
As some others have noted, it very well may be the gauges were not accurate. Look at line #11 - the test hydrant is noted to be at 238' elevation, and the Flow hydrant at 308' (70' higher). That 70' elevation difference should work out to be a 30 psi lower static pressure at the flow hydrant, compared to the static pressure at the test hydrant. The static reading (24 psi) is 45 psi lower than the static at the test hydrant. Something is amiss - I would have the contractor re-do the flow test and, if possible, witness the flow test.
Reply
Jerry Graupman
2/19/2025 10:50:06 am
Pitot pressure can NEVER be higher than static pressure.
Reply
2/20/2025 12:42:11 am
Sometimes, errors with readings and calculations are made. There are many potential causes.
Reply