|
For a fire sprinkler system, if you have a loop running around a typical hip-roof attic, and you have a center riser, can you tie it into the loop in two locations?
NFPA 13 doesn't really discuss when a looped system turns into a gridded system. None of the branch lines would be connected, so in my opinion this would be acceptable as long as you meet the discharge time through the remote inspector's test connection. What are your thoughts? Is this a gridded or double-loop systems? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Pete H
3/17/2025 06:33:27 am
As long as no branch line is directly fed from two sources, I would say it is not a grid and still is just a weird "double loop".
Reply
Anthony
3/17/2025 08:06:34 am
I'd argue that you have a "compound main" in a looped system. As long as there isn't a way for air to get trapped then you should be fine.
Reply
Casey Milhorn
3/17/2025 08:13:02 am
Yeah, probably stretching it a little bit. Many moons ago I had several projects where it made sense to create a double loop setup in a dry attic scenario. From memory, they varied from 500 gallons to 900 gallons. We ended up with accelerators AND exhausters on a few of them, and on one in particular we installed check valves at the fork on the first loop, just to meet water delivery times. Basically that allowed one side to be the path of least resistance and trapping the air in the other half of the loop, which kept it from being filled by water during the initial trip. Might be worth running this through Tyco's water delivery time program, but I'm not sure it can handle a double loop? Good luck!
Reply
Dave L.
3/17/2025 10:53:07 am
Ha, also done it (check valves) many moons ago. Now NFPA requires such check valves to be located in a heated enclosure and 1/8 in. dia. hole drilled in the clapper. (8.2.4.6 in the 2025 ed.)
Reply
Glenn Berger
3/17/2025 08:14:25 am
Yes, you can tie your riser into the loop at multiple locations. However, you did not indicate that the system is/was wet-pipe or dry-pipe. Since you asked about gridded systems, there is some implications that you do have a dry system and then you just need to ensure that air can be exhausted from the system and will not cause additional time delays.
Reply
Dan Wilder
3/17/2025 08:27:45 am
As you discuss discharge (delivery) time, I'm thinking this is a dry (likely) or preaction (not likely) system.
Reply
Jack G
3/17/2025 11:50:31 am
A loop is allowed( 2 paths) a grid is not ( more than 2 paths).
Reply
Robert Hughes
3/17/2025 12:53:44 pm
It is a looped system with two feeds.
Reply
Jesse
3/17/2025 06:48:41 pm
Agree this being a "loop" and not being a grid. I'd be interested to know the overall size of the system and the trip time.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop Sept '26 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
October 2026
PE PREP SERIES |
RSS Feed
