15x15 Sprinklers Spaced at 21.3-ft Along Branch?

10/30/2026

7 Comments

 
In NFPA 13, the maximum distance for standard coverage sprinklers is 15 feet, with a maximum spacing for light hazard of 225 sq ft.

If the ceiling and bar joists are at a
45-degree angle, why couldn’t the sprinklers be spaced 21.252 feet ( on the branch ) and between lines, as long as the pattern in the ceiling is 15 x 15?

It makes it easier to hang the branches (
across the joists) rather than with the joists and needing trapeze hangers (every other branch line)?

As long as the hydraulics are calculated for the additional branch distances, this should work right?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Chad
10/30/2026 08:12:31 am

because you need to measure along the slope:

NFPA 13 (2025)


9.5.3.1.2
The maximum distance shall be measured along the slope of the ceiling.

9.5.3.1.3

The maximum distance permitted between sprinklers shall comply with the value indicated in the applicable section for each type or style of sprinkler.


Handbook commentary:

The spacing of sprinklers along branch lines depends on the maximum distance permitted between the sprinklers on branch lines and the maximum area of coverage permitted per sprinkler. To minimize the amount of piping used, branch lines usually are spaced as far apart as possible, while maintaining even spacing within a ceiling bay or room. If the spacing of branch lines is uneven, the greatest distance between the sprinklers on the branch lines, measured between the centerlines of the sprinklers, should be used to determine how far apart sprinklers can be spaced from each other along the branch lines.

When defining the area of protection of a sprinkler installed under a sloped ceiling or roof, a common question is whether the area of protection is measured along the slope or along the projected area on the floor.

The spacing of sprinklers is measured on the slope of the roof, and the maximum distances and areas given in Chapter 10 through Chapter 15 are applied to the distance measured along the slope. For curved surfaces, the distance should be measured along the slope projected between the two sprinklers, as indicated in Exhibit 9.19

Reply
chad
10/30/2026 08:16:16 am

Also do not forget to apply a 30% increase in design area if unobstructed construction when slope exceeds 2 in 12 per 19.2.3.2.4

Reply
Glenn Berger
10/30/2026 08:20:17 am

Sounds like someone is using Pythagorean Theorem on us today.

See NFPA 13 Figure 10.2.7.1.3.1(a) and related material. - Looks like this subject is covered in this section.

Reply
Jesse
10/30/2026 08:33:47 am

I was told there'd be no math on Fridays....

The one thing I'd add is that the standard doesn't take into account things such as the ease of install. If the 15x15 doesn't work, maybe see if Extended Coverage will work

Reply
Dave
10/30/2026 12:36:42 pm

"I was told there'd be no math on Fridays." LoL :-)

But E.C. only if listed for that slope. And I found it interesting that NFPA 13 is going to allowing vertical orientation of sprinklers (like FM), not necessarily perpendicular to slope.

Reply
Dan Wilder
10/30/2026 08:36:15 am

Other than NFPA stating sprinklers shall be spaced along slope for distance but spaced horizontally for calculations...and there has not been any successful testing to prove your process.

While not intimately involved in the listing and approval process, the water distribution over the area likely does not meet a consistent minimum GPM/FT² at that angle (typically at 7PSI). These tests are based on a single sprinkler's distribution pattern so you could not rely on an adjacent sprinkler to "cover" the shortfall of another sprinkler.

http://www.firefoam.info/resources/White-Paper-NFSA-Sloped-Ceiling-Analysis.pdf

The setup for the test is literally a square collection grid on the ground that measures the water distribution over an area. While not a great video at all, the beginning of the below link shows the test grid on the ground and a test setup (the US based facilities I have been to have tubing beneath to collection units to measure the GPM over that corresponding area-but no pictures allowed)

https://www.youtube.com/watch?v=Zbj3H1-yG3w

If you have ever put a circle around a 15x15 square, the sprinkler coverage area it actually sprays a little over a 10'-6 radius, but the consistent GPM is within that 15x15 area.

Also, at that angle fire dynamics change from an outwardly expanding heat plume to a more linear and condensed straight line up the slope which also plays havoc on activated sprinklers since the heat plume gets pushed all over.

https://www.fm.com/-/media/project/publicwebsites/fm/files/resources/research-technical-reports/slopedceilingtestingreportreleasecandidate.pdf

https://www.fm.com/-/media/project/publicwebsites/fm/files/resources/research-technical-reports/slopedceilingtestingreportreleasecandidate.pdf

Reply
Jack G
10/30/2026 03:56:38 pm

It does work , even mathematically without additional trapeze and EQ braces.
Problem is……it’s against the rules.
You might be able to get The AHJ to buy into it for EQ and or Trapeses required. That might be your best shot!

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT