Sprinkler is being installed in a warehouse as part of a "base building" phase.
There are 1-inch outlets being proposed as the outlets on branch pipe, but a potential tenant is requesting a system that may require K16.8 ESFRs. Are tenant fit-out sprinklers permitted to be installed over bushings in this situation, by code? There will be a 5-year tenant lease, but no guarantee of resigning or extension on the tenant. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Pete H
7/21/2025 06:22:06 am
Why would this need a bushing? Most 16.8k heads are 3/4".
Reply
Jesse
7/21/2025 08:12:51 am
In remodeling a shall system for a finish-out, my standing order is to always match the existing K-factor or calculate the system changes. Most K=16.8 sprinklers are 3/4" and some are 1".
Reply
NK
7/21/2025 08:13:44 am
ESFR sprinklers arent that much more expensive than standard spray sprinklers for new construction. I'd talk to the building owner about using K25 ESFR or K16.8 ESFR sprinklers for the base building to simplify/minimize future sprinkler modifications as tenants change. This is much simpler than what you're describing (which sounds like something that was requested by someone that probably doesnt understand what they're requesting) and will also help with ESFR obstruction considerations early on in building construction which will also helpful for the owner.
Reply
Chad
7/21/2025 08:48:36 am
I second this, max out the demand around water supply and dont have to change it later.
Reply
Dan Wilder
7/21/2025 08:22:20 am
13-19' Edition
Reply
Glenn Berger
7/21/2025 08:35:21 am
NFPA 13 - The 2025 version revamp the clarity of utilizing bushings from the 2022 version (which had been in the standard for a significant period of time). In the 2025 version see Section 30.5.2.1.
Reply
Ricardo Gonzales Jr
7/21/2025 09:01:57 am
I would recommend doing a sample diagram and see what the system calculates out as. You'd spend more time to justify the smaller pipe than to do a sample system. Then you'd have backup for your decision.
Reply
danefre
7/21/2025 09:06:13 am
Careful with this as it's a pretty common request from owners that don't understand the ESFR requirements.
Reply
Jack G
7/21/2025 12:26:24 pm
Personally I feel that using a large k factor sprinkler in a tenant space or combo warehouse tenants fit out is a no no.
Reply