1-Hr Rated Wood Ceiling Need Sprinklers Within?

9/4/2025

6 Comments

 
I have a mixed-use building, retail ~6250 square feet on the ground floor with residential occupancy on the 2nd and 3rd floors. The building is a mix of wood construction with bar joists, with a ceiling attached to the bottom chord of the bar joist.

These bar joists have the bottom and top chords made of wood with 1" steel tubing to create the open bar joist.

My question concerns 2016 NFPA 13, Section 8.15.1.2.4.

Can I classify these open hybrid joists as noncombustible bar joists?

The ceiling is flat without access to the space. The ceiling assembly between the retail and the 2nd floor residential is 1-hour rated.

The big question is, can we use the exception 8.15.1.2.4 and not provide sprinklers in the space above the ceiling?

If not, I was told that if the ceiling assembly was two hours that the sprinklers in the concealed space can be eliminated. I haven't been able to find this in the NYS Building and Fire Codes.

Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Pete H
9/4/2025 06:02:38 am

NFPA 13 (2016) 8.15.1.2.4 - Concealed spaces formed by bar joists with less than 6" between the roof or floor deck and ceiling shall not require sprinkler protection.

-

I'm not really concerned about the joists combustibility (we already accept the spaces is a concealed space) but about the distance for this exception.

If it is less than 6", the exception applies.

-

That said, I think you were asking about 8.15.1.2.5 Concealed spaces formed by ceilings attached directly to or within 6" of wood joist or similar solid member construction shall not require sprinkler protection.

Especially with the line "With a ceiling attached to the bottom chord of the bar joists."

Which also has the Annex note:

A.8.15.1.2.5 - Solid metal purlin construction with a wood deck is one example of similar solid member construction.

-

Obviously I cannot be certain, but that sounds like the more applicable exception

Reply
Streeter
9/4/2025 10:25:40 am

I think Pete is right that 8.15.1.2.4 would apply and I think you can omit sprinkler in these spaces.

But keep in mind that when using the exceptions for omitting sprinklers in concealed spaces you must increase your remote area to 3,000sf per 11.2.3.1.5.1.

Reply
NickG
9/4/2025 12:59:14 pm

So the fact that the bar joist are open with the sheetrock attached to the bottom chord, and not a solid Joist or solid member construction. Section 8.15.1.2.4 talks about Bar Joists which there is a distinction between bar joist and wood bar joists. section 8.15.1.2.16 addresses wood bar joist which states that the sprinklers can be omitted if non-combustible Batt Insulation fills the space between the bar joists. I would prefer to consider the space as concealed space and not install the sprinklers or the Batt insulation.

Reply
Wes
9/4/2025 04:02:46 pm

Just be careful, as there are two separate concepts being floated here.

The horizontal 'assembly' can be fire-resistance-rated, as an assembly. It can carry a 1-hour separation (or more). This is for the purposes of separating two areas for passive fire protection.

The rating is an entirely independent discussion than whether sprinklers are required.

Omitting sprinklers depends upon the standard being used (NFPA 13 vs 13R vs 13D), whether the space has combustible materials (it does), whether the space is concealed (it appears to be so), and whether there's an allowance to omit sprinklers within the space.

In this case, this sounds like it's an NFPA 13, combustible concealed space; in which case Pete cited the most probable path to omit sprinklers.


Swapping 1-hour FRR with NFPA 13 rules seem related, but they're two different concepts built for two different things.

Reply
Robert Morgan
9/4/2025 04:29:27 pm

I doubt the "hybrid" joist is less than 6", also keep in mind that filling the space with non-combustible insulation is to make it a non-combustible confined space, which would not require sprinklers. There are requirements for draft stopping that may apply also. Lastly, the wood can have a 1hr. rating IF it is used as part of an assembly (fire retardant treated wood). Just using this alone does not make a rated separation. Like others have stated, this rated separation is for the R/B,M use groups, not to omit sprinklers.

Reply
Jack G
9/15/2025 06:30:27 pm

The following prohibits 13r, 13 d:
1. Area increases due to sprinklers
2.rating reductions due to separated occupants, type VA construction ,corridor walls.
3. Miscelanous-- hazardous material increases, high rise modifications, atriums,, limited area buildings, allowable area of openings, residential floor draftstopping ( if sprinklers not extended into affected areas), other group draftstopping, ball
4. VB construction is limited to 2 story for 13 d

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT