By Jocelyn Sarrantonio, PE | Fire Protection Engineer / Technical Director at MeyerFire Although the 2024 editions of the International Building and Fire Codes have been out for some time, new codes don’t get used until a jurisdiction adopts them. Now that I’m starting to see them referenced more often in project work, it feels like the right time to dig into what’s new. The humor is not lost on me that, as we begin to wrap up 2025, I’m finally getting deep into the changes to the 2024 codes. No better time than now to review the changes in the 2024 IBC Before we get started, if you haven’t taken the MeyerFire University LS111 course [here], it’s a great series on Effective Use of Codes & Standards. One of the many helpful items that Fire Protection Engineer Sean Donohue reviews is how to tell code language has changed. Not to be all “back in my day”, but when we only had the print and PDF editions of codes, we were used to seeing the vertical bar near new sections of code. Now, since most of us use the online versions, we should realize that new text is indicated in blue text, deletion arrows (→) are used for deleted text, and stars (*) for relocated text. The intent here is not to cover every single change here, but to highlight some of the provisions that may impact the day-to-day workings of someone in the fire protection engineering profession. As always, and I really cannot emphasize this enough, check your local amendments. Very few jurisdictions will adopt the codes outright; they’ll often make some changes. OCCUPANCY CLASSIFICATIONS (CHAPTER 3) While the official classification of occupancies is typically up to the architect, it’s important to know what to expect with these changes. It will come as no surprise that changes have been made to certain occupancy classifications due to their use of lithium-ion batteries in energy storage systems (ESS). Examples include:
Manufacture and storage of electric vehicles now classified as Group F-1/S-1 What’s the impact here? To start, the F-1/S-1 designation is for moderate-hazard, and the F-2/S-2 classifications are for low-hazard occupancies. These classifications are helpful, as the occupancy classification of areas using ESS could fall into a bit of a no man’s land. ESS regulated by IFC Section 1207 would be exempt from regular Group H requirements, so prior to this change in IBC 2024, there wasn’t much direction on what to classify these occupancies as. Since “electrical rooms” aren’t listed in Chapter 3, generally I would see large UPS or Electrical Rooms be classified as either Group B, F-2, or S-2, maybe matching the predominant occupancy of the building. However, classifying these spaces as the more hazardous designation of Group F & S has a trickle-down effect for the rest of the fire protection features. There are differences in allowable areas, separations for mixed-use occupancies, and means of egress requirements between Group F-1/S-1 and Group F-2/S-2. For example, in a sprinklered F-1/S-1 occupancy, travel distance is limited to 250 ft, as opposed to 400 ft for F-2/S-2 occupancies. Another important implication would be for smoke and heat removal. Section 910.2.1 requires smoke and heat vents, or a mechanical smoke removal system for Group F-1/S-1 occupancies with more than 50,000 square feet of undivided area. That may seem like quite a large area, but data centers can easily exceed this limit. And I’m sure you could guess that if I have a giant room full of servers and specialized equipment, the last thing I want is multiple roof penetrations overhead. Smoke and heat vents required for certain Group F-1/S-1 occupancies As we’ve covered in our two ESS courses, these additional safety features are well warranted due to the risks presented by lithium-ion batteries. And to be fair, the ventilation system I am probably providing for my ventilation and explosion control probably counts as a “mechanical smoke removal system”. But the point here is that it’s important to think of the ripple effects of seemingly small and straightforward changes. The change is contained in Chapter 3 for Occupancy Classifications, but it trickles down to items in Chapters 5, 6, 9, and 10. CHAPTER 9, SECTION 903 CHANGES The next place where we’ll see some big changes is in Section 903. We do have an IBC Cheatsheet that lists when sprinklers are required per Chapter 9, which you can find below. The cheatsheet includes footnotes for new provisions in 2024, but it should come as no surprise that many of the provisions are for occupancies that use lithium-ion and lithium metal batteries. These include:
An additional change is the design parameters for the sprinkler system, when it is required, to protect these areas containing lithium-ion or lithium metal batteries: “… design of the system shall be based on a series of fire tests. Such tests shall be conducted or witnessed and reported by an approved testing laboratory involving test scenarios that address that range of variable associated with the intended arrangement of the hazards to be protected.” -IBC 903.3.1.1.3 Sprinkler System Design for lithium-ion batteries should be based on fire testing That’s pretty explicit language here, which is extracted from the fire code. There is no one-size-fits-all solution, and the system design should be based on fire testing. But because we’re fire protection folks we know that we probably aren’t going to have all of that information at the time we need it. It would be great if we had fire testing data for all of the items that would be stored in a given facility, but we know that’s not realistic. In this case I would defer to the Fire Code, which in Section 1207 lists a sprinkler system density consistent with Extra Hazard Group 1 for certain situations. If I don’t yet have testing information, that’s a safe density to use so I can start planning my water supply and sizing my pump. OTHER CHANGES OF NOTE Even though pixels are basically free, this post would become unreadably long if we went in depth for each change! To summarize the rest of the IBC 2024 changes of interest:
And similar to the sprinkler changes for areas with lithium-ion and lithium-metal batteries, a fire alarm system required, activated by air-sampling or radiant-energy sensing detection systems, for the following areas:
Once we get into Chapter 10 for Means of Egress, one notable change includes:
Lower exit signs are exempt from sprinklered Group R-1 occupancies Like every new iteration, this code cycle brings a mix of fine-tuning and forward-thinking. Many of the 2024 reflect something that’s not new: the emerging risks of energy storage systems using lithium-ion batteries. But there are plenty of smaller tweaks, including the visible sprinkler system alarms and standpipe hose connections in exterior stairs, which will find their way onto our next set of plans too. Even seemingly small changes, or those that we think are “out of our scope” may have big downstream effects that impact all of our design and construction partners.
What other changes to the 2024 IBC and IFC have impacted your projects? Comment to share your stories below. Thanks for reading, and remember to keep learning, because the code never stops changing! - Jocelyn
Anthony
11/12/2025 09:00:11 am
907.2.2.2 and 907.2.4.1 is requiring Vesda as well that's a non trivial cost added to these facilities. Comments are closed.
|
ALL-ACCESSSUBSCRIBEGet Free Articles via Email:
+ Get calculators, tools, resources and articles
+ Get our PDF Flowchart for Canopy & Overhang Requirements instantly + No spam
+ Unsubscribe anytime AUTHORJoe Meyer, PE, is a Fire Protection Engineer out of St. Louis, Missouri who writes & develops resources for Fire Protection Professionals. See bio here: About FILTERS
All
ARCHIVES
September 2026
|
RSS Feed