Has Forward Flow Testing Turned the Corner?

10/28/2026

6 Comments

 
​One of the most-cited articles we’ve had covers how to adapt an existing sprinkler system to accommodate the required Forward Flow Test for backflow preventers in fire sprinkler systems. 
 
At the time, we saw Forward Flow as the most “overlooked” requirement in fire sprinkler system installations and regular testing. It’s been required since the 2002 Edition of NFPA 25, but even the NFPA 25 annex commentary acknowledged a historical lack of enforcement. 
 
OVERLOOKED NO MORE? 
Well, the vibe (as the kids would say) today seems to be that the days of being overlooked may be ending. 
 
Why? 

What’s the difference between today and 2018, or the decade and a half before that, when the test and the means to do the test were mostly ignored? 
Picture
In order to properly conduct a Forward Flow Test, where the whole system demand is flowed through a backflow preventer, there has to be a means within the system to do so. The problem with getting the Forward Flow test to happen is in part policing it, but mostly adapting existing systems to have the ability to easily run the test. We explore ways to adapt systems for the Forward Flow Test here.

It could be three things - insurer awareness, AHJ enforcement, and electronic inspection reporting. 
 
#1 INSURER CITATION 
Insurers care that systems can actually work. The risk without Forward Flow tests is that a backflow preventer that hasn't been properly exercised could stay closed when it's called to perform. If the backflow preventer can’t fully open, it’d strangle the system’s supply. 
 
What I find interesting is that while this test serves to check on the working ability of the backflow preventer, the test also functionally tells us a whole lot about how much water actually makes it to the riser as it should. If we put a couple calibrated gauges on the backflow while we do the test, we can even compare our original design to what's happening in reality. 
 
Anecdotally, more insurers seem to be looking to the forward flow test for validation that enough water, at enough pressure, can generally make it into the system. They can drive the need to make the test happen. 
 
#2 AHJ ENFORCEMENT
Are AHJs more aware of the requirement today than a decade ago? Possibly.

It doesn't hurt that it's been discussed and that many contractors have already corrected systems for the ability to perform the test. This is hard to measure, but anecdotally I’ve found that the more an inspector or reviewer is aware of an issue, the more a requirement is enforced. 
 
#3 BETTER REPORTING SYSTEMS
Perhaps the biggest driver in the conversation automated and standardized reporting.
 
What used to be handmade or contractor-specific form that only went to the owner has started to give way to standardized forms that automatically submit results to the local jurisdiction. 
 
Maybe old forms didn’t have a byline for forward flow. Not anymore.

Now, many AHJs require electronic submission and tracking of all inspection, testing and maintenance reports. Inspections using Inspect Point, ServiceTrade, BuildingReports, Ember and many more submit and provide standardized reporting to AHJs as soon as the inspection is complete. 
 
Picture
Many custom-built paper inspection forms that only used to get sent to the building owner are now electronic, standardized, and are required to be submitted to the AHJ. The result is more transparency and an easier ability for AHJs to see and track deficiency corrections.
 
What may have never made it to an AHJ before is now a report AHJs see and track. Those gaps are visible, transparent, and easier to enforce.
 
WHY HASN’T IT BEEN DONE HISTORICALLY?
Why is this even a talking point?
 
First, in order to conduct a Forward Flow test and flow enough water to meet the system demand, we have to have a way to flow it. Not all systems, especially older systems, have hose connections or a test header to flow enough water through. There’s no way to perform the test without flowing out the fire department connection (not easy and requires shutoff, draining down, reversing a check valve, holding clapper(s) open, shutoff, drain down, re-reversing the check valve, and refilling the system).
 
Without an easy way to conduct the test, contractor’s haven’t gone through the lengthy effort of doing it.
 
Why not flag it and recommend or require the owner to add a means for forward flow?
​

Picture
A means to conduct a forward flow, like adding hose valves downstream of the backflow preventer, can allow Forward Flow Test to be conducted more easily in the future. 
 
More anecdotal observation here, but for the most part, some contractors worry that their competitors aren't doing it and they’ll potentially lose the customer if they flag it and "get shopped around."
 
That, or the test and means to do the test have been neglected for so many years that it’s painful to bring it up now. “Twenty years and this has never come up, why now?” What’s our answer to that?
 
The short answer more and more - is that it's now being enforced.
 
WHY DOES THE TEST MATTER IN THE FIRST PLACE? 
I once was on a new construction 3-story dormitory with a wet pipe fire sprinkler system. We did our acceptance testing as usual. Flow switches? Around 45 second responses, great. Tampers, great. Main drain? Recorded. Static pressure on the riser gauges, even the main drain residual pressure – looked fine.
 
But once we tried the forward flow, opening just one 2-1/2” hose valve on the backflow test header… we hardly had a trickle.
 
Opened up the 2-1/2” hose valve on a dedicated test header all the way – it hardly dumped through our Little HoseMonster. We couldn’t even register a 1 psi pitot reading on the discharge hose.
 
What in the world?
 
This building had a 6-inch service main to it. It should be gushing out of the hose, especially with just one 2-1/2” that was open.
 
We went to the street and tested the hydrants again. Flowed great, same as about a year prior during design.
 
Looked at the gauges on the riser. Static pressure looked fine.
 
Checked the gate valve at the street. Turned it all the way closed and all the way open. Same thing.
 
Well, after 2 months of back and forth, the line was video-scoped, and it turns out the tap made at the street had drilled the ¾” pilot hole into the street’s main, but the drill never actually removed the rest of the 6” coupon on that tap. The entire system was being throttled where the 6” main meets the street, all the way down to one ¾” opening.
 
Picture
A 6-inch service had been installed but the 'hot tap' at the street was never drilled more than the 3/4" pilot hole. As a result, water could fill the sprinkler system and static pressure showed fine at the riser, but the entire system was throttled to a single 3/4" opening. It likely would never have been discovered without a Forward Flow Test.

Had it not been for the forward flow test, would we have ever known?
 
“Oh well, you should tell that from the main drain test.” How? The residual was a normal ~5 psi below the static, and it was the initial Main Drain test. There’s not a right or wrong there – in fact, we would have incorrectly set the benchmark for future Main Drain tests forever had we not found this problem.
 
“Well, where was the coupon? How did the contractor not provide the coupon?” That’s fair, but plausibly, how often do you get the underground contractor to provide a coupon? How often do you actually see it? I struggle to get any kind of underground documentation on hydrostatic and flushing – are you always getting pipe coupons shown to you during inspection?
 
I don’t expect inspectors, nor contractors, to be perfect. That’s why we have inspections and tests – to verify and validate systems. The forward flow test, uniquely, can tell us a lot about our systems that we otherwise wouldn’t know after an install.
 
Without that forward flow test, would we have had 40 or 50 years of a dormitory building protected by a sprinkler system that’s throttled through an opening the same size as a hose?
 
It’s possible, and scary to think about, honestly.
 
I tell the story because the test is both a required and necessary part of the functionality for a fire sprinkler system.
 
HOW TO CREATE A MEANS FOR FORWARD FLOW?
There are a few ways to do this, but as an industry I think we can clarify this a bit better. How can the means be added in the simplest, best, and/or least expensive way?
 
Second, is how do we get that information in front of contractors and owners in a way that’s really easy to price?
 
Third, how do we support jurisdictions in consistent enforcement? 
 
In my opinion, we have an opportunity today with the growing awareness and the more centralized reporting systems to clean this up for good. If AHJs have backing in their enforcement (multi-organization recognition and public position statements), where contractors can have confidence that everyone is playing by the same rules, then we can get systems corrected and have the ability to fix this going forward.
 
This topic was brought up and I’m fortunate to be working in a collaborative effort with local fire marshal representation and NFSA to build some kind of utility (whitepaper, tool, position statement, or something in that vein) – that serves to support all the parties in getting this right.
 
If you have a take – objections to why it’s done – difficulties in getting corrections – ideas for how we can fix it as an industry – tools that would be nice to have at your disposal, comment below or shoot me an email at [email protected].
 
Thanks for reading – more to come on this!
 
Joe
6 Comments
Kathleen Balch
10/28/2026 11:10:44 am

Thank you for writing this article. It reinforces everything we have researched, studied, and implemented regarding forward flow testing.

We have made forward flow testing a standard part of our inspection procedures and have installed numerous hose valves on existing systems to allow us to properly perform these tests.

Our customers have been very receptive, and we have not experienced any objections. We firmly believe that by taking these additional steps, we are providing a higher level of service and helping ensure our customers' fire protection systems operate as intended.

It's encouraging to see an article that supports the practices we have worked hard to put in place.

Reply
Dave
10/28/2026 12:23:11 pm

I'm glad NFPA eventually provided clarification on what testing arrangement was acceptable. One contractor I worked for made me just provide a grooved outlet with a cap, saying "There's your means." One of the very few disagreements I had with a later FPE boss was that in his specs he required the test to be a means to verify the backflow curve, complete with requiring signage to be posted indicating the pressures during the test and pressure curve data. We do require a normally-closed valve prior to the hose valves, requiring me to make sure the normally closed version was actually submitted on, ordered, and installed.

Reply
Jack G
10/28/2026 03:43:39 pm

Thank you again for this discussion article. I ve run into the coupon still in the tap quite a few times so that would be what I suspect first. Usually happens when the water company has the lowest bidder doing the tap.
I try to be there when the tap is being made. The coupon is a problem along with flushing and testing and a flushing and testing certificate are other issues,
In Trenton nj, the plumber gave a certificate to the GC for us. We had a big diesel pump—- package.
Our fitter , while filling heard rumbling in the inside supply as we filled.
Took the supply pipe apart, about 80 ft of 8 inch filled with gravel. Took pipes, fire pump apart to remove gravel. They blamed it on the street construction, where the tap and testing was made.
. Boy did I moan. The gravel continued about 60 ft past the pump.
We received change orders but what aggravation.
From that point on about 15 years ago, I flush and test the underground whether it’s in my contract or not. And refuse to tie into it unless we do.

Reply
Dale Morris
10/28/2026 03:51:27 pm

For me, it was several RFI's from the same FP contractor. I replaced another Engineer, and was picking up several projects already under construction. I swear the FP contractor had the RFI set up as a form, and as soon as the project got under way for the sprinkler work, here comes the same RFI; RFI #1, asking about don't we need forward flow testing? I had it 4 times. At least I was able to stop the madness on projects going forward for this client, but the sting has stayed with me!

Reply
Mike Slaughter
10/28/2026 04:06:09 pm

Is forward flow testing required for both a 13R and a 13 system, or merely a 13 system?

Reply
Chris Beleal
11/6/2026 08:39:31 am

How would a main drain test only drop the residual pressure 5 psi if there was only a 3/4” orifice at the street tap allowing water to pass? This doesn’t make any sense to me. I would question how long the main drain test valve was open. If it was open for even 60 seconds, not only would the residual pressure drop beyond 5psi, but the return to static pressure once the drain was closed would be noticeably slow considering the 3/4” supply orifice, which would indicate a potential obstruction. In fact, there are many times when a forward flow test in a residential or light hazard occupancy can be achieved through the main drain test, since the most demanding sprinkler system flows are generally very low volume. This doesn’t have to be guesswork either, the main drain flow capabilities are able to be determined in most design software programs so you know whether additional means of flowing water are necessary to achieve the forward flow test of the most demanding hydraulic calculation.

Reply



Leave a Reply.

    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET THE TOOLKIT

    SUBSCRIBE

    Get Free Articles via Email:
    + Get calculators, tools, resources and articles
    + Get our PDF Flowchart for Canopy & Overhang Requirements instantly
    Picture
    + No spam
    ​+ Unsubscribe anytime
    I'm Interested In:

    AUTHOR

    Joe Meyer, PE, is a Fire Protection Engineer out of St. Louis, Missouri who writes & develops resources for Fire Protection Professionals. See bio here: About


    FILTERS

    All
    AI
    Announcements
    Author Jocelyn Sarrantonio PE
    Book Review
    Calculators
    Career
    Course
    Delegated Design
    Design Challenge
    Detail Critique
    Fire Alarm
    Fire Events
    Fire Suppression
    Flammable & Combustible Liquids
    Flexible Drops
    Floor Control Valve
    Life Safety
    News
    NICET
    Opinion
    Passive Fire Protection
    PE Exam
    Perspective
    Pick A Part
    Pick-A-Part
    Products
    Site Updates
    Special Hazards
    Specifications
    Sprinkler Systems
    Standpipes
    Students
    Talks
    Tools
    Videos


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    January 2025
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    December 2020
    November 2020
    October 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    April 2018
    March 2018
    February 2018
    January 2018
    December 2017
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    May 2017
    April 2017
    September 2016
    August 2016
    July 2016
    June 2016
    July 2015
    June 2015
    May 2015

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT