MeyerFire
  • Blog
  • Forum
  • THE TOOLKIT
    • SUBMIT AN IDEA
    • BACKFLOW DATABASE*
    • CLEAN AGENT ESTIMATOR*
    • CLOUD CEILING CALCULATOR
    • DOMESTIC DEMAND*
    • FIRE FLOW CALCULATOR*
    • FIRE PUMP ANALYZER*
    • FIRE PUMP DATABASE*
    • FRICTION LOSS CALCULATOR
    • HANGER SPACER*
    • IBC TRANSLATOR*
    • K-FACTOR SELECTOR*
    • NFPA 13 EDITION TRANSLATOR ('19 ONLY)
    • NFPA 13 EDITION TRANSLATOR ('99-'22)*
    • LIQUIDS ANALYZER*
    • OBSTRUCTION CALCULATOR
    • OBSTRUCTIONS AGAINST WALL*
    • PLUMBING FIXTURE COUNTS
    • QUICK RESPONSE AREA REDUCTION
    • REMOTE AREA ANALYZER*
    • SPRINKLER DATABASE*
    • SPRINKLER FLOW*
    • SYSTEM ESTIMATOR*
    • TEST & DRAIN CALCULATOR
    • THRUST BLOCK CALCULATOR
    • TRAPEZE CALCULATOR
    • UNIT CONVERTER
    • VOLUME & COMPRESSOR CALCULATOR
    • WATER STORAGE*
    • WATER SUPPLY (US)
    • WATER SUPPLY (METRIC)
  • UNIVERSITY
    • JOIN
    • CATALOG
    • CONTENT LIBRARY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE Prep Series
    • PE 100-Day Marathon
  • LOGIN
  • PRICING
    • SOFTWARE & TRAINING
    • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

New Live Fire Sprinkler Remote-Area Analyzer

6/3/2020

 
When I initially set up a hydraulic calculation for a tree-style sprinkler system, there are a few key points I have to consider. All of these points today and the tool are specifically for tree systems (not gridded).

First, we need to determine what the remote area actually is. In NFPA 13, for instance, there are multiple adjustments (quick-response sprinklers, dry systems, sloped systems, high-temperature, etc.). Even if we start with a 1,500 sqft remote area, it could look a lot different after multiple adjustments.

Second, we need to determine the minimum length of the remote area along a branch line. This is a relatively straightforward at 1.2 x √ (remote area size), but it's still another hand-calculation that needs to take place.

We then round up to determine the sprinklers along the first branch line, then expand by branch lines to figure out how many sprinklers are actually in a calculation.

The tool I'm introducing today (which is also now available on the Toolkit) is a schematic-level remote area analyzer that will apply multiple adjustments and quickly estimate the important parameters associated with a remote area.

With only a few quick inputs, you'll see an initial remote area laid out with a live schematic of your situation. Click either of the images below to give it a try:
Picture
Picture
A new remote-area analysis tool which incorporates adjustments and gives a live schematic layout. See it here.
If you already have the toolkit, you can download this and three other recently added tools in today's Toolkit update here. If you're interested in giving this tool a try, check it out here. I'll have it up without any login credentials for a couple months.

In time, I'm looking forward to expanding this tool to have some powerful estimating abilities. 

Any suggestions, tips or feedback? Post a comment or shoot me an email at joe@meyerfire.com. 

A Hurting World at Large
Just like I don't ask hollywood to be my moral compass, you don't come here for my my personal opinions. I get it. That said there has been a tremendous amount of unrest here locally, nationally, and worldwide this past week.

I think there's a major feeling that our collective perspective has to improve. I want to do better and be part of a better future for everyone. I want you to know that whoever you are and wherever you are, I very much care about you and your well being. You have tremendous value. Hope you and yours are safe, healthy, and doing well.

Thanks & I hope you have a great week.

New Updates to The Fire Sprinkler Database

5/28/2020

 
Did you know there are over 1,500 variations of sprinkler models which are actively on the market today?

Around three years ago we began development on one of the largest research projects we've ever undertaken - organization of all the fire sprinklers available on the market today. It took several hundreds of hours to finely comb through all the k-factors, pressure listings, spacing distances, model numbers, responses, and links to websites and product data.

​The Comprehensive Fire Sprinkler Database
In late 2018, we finally released it - a comprehensive Fire Sprinkler Database. With it you can search by SIN, k-factor, type, spacing distances.... most any parameter you need to in order to find the sprinkler that's the best fit for your design.

​The introductory video to it is here (forgive the terrible voice narrator... it was me): https://www.youtube.com/watch?v=DsLPg4GKaCU

Updates from This Week
Just this week we've updated the database to include recent releases for new sprinkler models from Tyco, Viking, and Reliable, including new window sprinklers, concealed sprinkler options, MRI sprinklers, institutional sprinklers, and corridor sprinklers.

Use It Today
If you haven't checked it out - here's an opportunity to do so. I've opened it up for everyone just for the next couple weeks. Just go to this link - www.meyerfire.com/sprinklerdatabase - and login using info@meyerfire.com as the username and sprinklerdatabase as the password if you're not already a Toolkit subscriber.
Picture
The Fire Sprinkler Database is the most current and comprehensive database of available fire sprinklers across all manufacturers we know about. Click the image to login and try it out.
What's Next?
For those in the inspection department - it's been asked how we can take this to the next level.

Can we get obsolete and recalled sprinklers into the database as well, so that we can quickly search to find information on recalls? That answer is yes, but I need your help. I'm not regularly involved in inspections, but I know many of you are.

If you have a good understanding of where all the various manufacturers recall information (old and current companies) and how I could best showcase that material, please reach out to me at joe@meyerfire.com. I'd be happy to get some input on how I can tackle this next phase of the database and make it that much more useful for us all.

​Thanks & have a great week!

Updated Obstructions PDF Cheatsheet

5/7/2020

 
A couple weeks ago I sent a sprinkler obstructions cheatsheet for the options with standard spray sprinklers and ceiling-mounted obstructions where the sprinkler cannot throw over the obstruction.

Thanks to some great suggestions, I've now incorporated some visuals that might help. As always, thanks for the feedback! You can download the updated cheatsheet here:
​
DOWNLOAD OBSTRUCTIONS PDF CHEATSHEET
Picture

​A New, Free, Fire Protection App
In case you missed it last week - there's a new free fire protection app on the market.

It's free and was developed by Michael Swahn and the helpful engineers over at Sebench Engineering out of Atlanta. It's now live on both Google Play Store and the Apple App Store. Here's links to get it:

Apple: https://apps.apple.com/us/app/sebench-engineering/id1506207375
Google Play: https://play.google.com/store/apps/details?id=al.pragmatic.sebench.android
 
The app has quick-calculations for Fire Pump Tests, Hydrant Flows, Equivalent K-Factors, Flow/K-Factor/Pressure Calculations, and Friction Loss. Download it today with the links above.
NFSA Expert of the Day Handbook Coming Summer 2020
One of the major projects I've been working on since last fall is development of the National Fire Sprinkler Association's Expert of the Day Handbook. It is a two-volume hardcover compilation of thousands of informal interpretations by NFSA's Experts, spanning 2004 through 2018. 

The set will be available through NFSA later this summer (likely by July). I'm thrilled to be a part of compiling these in a searchable, organized manner that could very well be the go-to resource for suppression design, inspection & testing outside of the standards themselves. There will be plenty more on this as the book becomes available for sale, but wanted to share a little of the good news on this exciting undertaking. 

Thanks & I hope you have a safe and great rest of your week!​

The Fear of Asking in the Digital Age

4/29/2020

 
Earlier this week I read a very basic question on a sprinkler design forum. Some say there are no bad questions. Those hypothetical people may never have been in a Facebook Group.

The question clearly showed the lack of understanding on the part of the person asking the question.

You can imagine what happened next – the keyboard warriors went to battle. They had fun blasting the novice into the internet oblivion.
 

And this happens all the time.
 

It doesn’t have to be Facebook. It happens on Facebook for Businesses (also known as LinkedIn), email forums, Reddit, and other online technical forums.

It is also not limited to the digisphere. A bad question in a conference room or in the field gets chided at best or embarrassingly criticized at worst.
 

Did we all not start somewhere with nothing?


I’m not a second generation Fire Protection Engineer, but my guess is those that are third and fourth generation practitioners don’t come out of the womb spelling escutcheon correctly.

I'm still not 100% convinced I spelled it right just now.

We all started knowing literally nothing. We each are on our own journey learning piece by piece and at different paces that never really ends. The best experts that have spent three decades in the industry are still always trying to improve.
 

Is there harm in asking a dumb question? Yes, but it’s not the embarrassment in the moment or the obvious display of misunderstanding. It’s the discouragement to ask the next question.

When Average Jim (I have to use Average Jim because Average Joe hits a little too close to home for me) actually seeks an answer to a basic question and gets lambasted – you know what he’s not going to do? He’s not going to ask the next five questions that he also needs answers on. 
 

On the very first morning of my very first internship, I asked a bad one. I was maybe 15 minutes into that first day when the site project manager asked me to make copies of a handful of documents. I asked if the staples had to come out before making copies.

Dumb question? Yeah. Do commercial copiers appreciate hard metal through their sensitive little feeder claws? No. And had I ever used a commercial copier before? No.

If I hadn’t asked, would I have been the dufus that destroyed a commercial copier 15 minutes into his first internship? Yeah brah, that would have been moi.
 

I heard so much crap about asking that question, but I was glad I did. I also never had to ask it again.

Eventually my questions got slightly more sophisticated and a little better, but I did start at nothing.

 
I’m not going to change human behavior. I can’t help people act online like they would in a face to face conversation.

What I can do is provide a better avenue for those people who don’t want to be vilified but do need answers to their question.

With nearly a couple decades of internet usage we know now that it isn’t Vegas - what happens on the Internet stays on the Internet. Like forever.

It’s getting more and more difficult to ask a question that isn’t tagged to your name, your company, or your reputation. Your forum question you wrote in 2007 when you didn’t know anything on pre-action systems? Yeah it’s probably still searchable.

Goodness knows I’d rather not have my kids go post-by-post from what I put on Facebook during high school. Same would go for a client seeing questions I would have had early in my career.
 

So what can I do about it now? Create a quality avenue for the question - any question - whether it’s expert-level or at square one - and not tie a personal reputation to it.

If you haven’t checked it out, the Daily Forum is a place for a single, filtered, anonymous question each day. There are experts there from a wide variety of backgrounds and locations that have far more knowledge than I could hope to gain.

Experts from across the globe, from AHJs to Designers to Researches to Installers to Engineers. Last I checked we were approaching nearly 3,000 subscribers just to those questions.
 

If you have a "dumb" question, if you don’t want to ask your boss, if you need an outside opinion, and you don’t want your identity tied to something it? Send us your question here. Also consider bookmarking the page so you can send in that question the next time you're stumped.

The link toward the bottom of this email “Have a fire protection question?” is always there for exactly that same reason.
 
Chances are, if you have an interest or can’t find an answer, someone else is looking for it too. When you ask, we all learn. And that’s exactly what this site is all about. 


Free NFSA Virtual Conference Tomorrow
This year's National Fire Sprinkler Association Business and Leadership Conference went Virtual. The virtual seminars are this week (Thursday the 30th and Friday the 1st). Registration is live, it is FREE, and CEUs will be awarded. Check it out here.

I had the pleasure to talk about the changing digital media opportunities in fire protection with the host of the Fire Sprinkler Podcast, Chris Logan, as part of the virtual conference. I believe we'll air at 2:35 pm Eastern Time on Thursday.
​

A New, Free, Fire Protection App
I've gotten asked a good handful of times - "Will you make an app?"

While I am quintessentially a millennial who disowns being a millennial, I have thought about making an app.

The good news is, there's already one that I was able to help beta test and can now share with you. It's free and was developed by Michael Swahn and the helpful engineers over at Sebench Engineering out of Atlanta. It's now live on both Google Play Store and the Apple App Store. Here's links to get it:

Apple: https://apps.apple.com/us/app/sebench-engineering/id1506207375
Google Play: https://play.google.com/store/apps/details?id=al.pragmatic.sebench.android
 
The app has quick-calculations for Fire Pump Tests, Hydrant Flows, Equivalent K-Factors, Flow/K-Factor/Pressure Calculations, and Friction Loss. Download it today with the links above.

Thanks & I hope you have a safe and great rest of your week.

New Sprinkler Obstructions Cheatsheet

4/22/2020

 
There are a handful of rules in NFPA 13 covering how sprinkler protection works in and around obstructions. It's for good reason; we don't want objects getting between a growing fire and our best method of suppressing it.

The PDF cheatsheet this week covers options for throwing water below obstructions, where the top of the obstruction is at or above the sprinkler deflector, for standard pendent and upright sprinklers.

If the sprinkler deflector has the ability to throw over the top of an obstruction - different rules apply - which we'll get to in the coming weeks. 

To get your free PDF download, enter your email below and you'll immediately have the PDF sent right to you. If you're already subscribed to the blog, check the Recent Resources section at the very bottom of your latest April email.

Picture
I'm Interested In:

​As always, any tips, ideas or feedback feel free to send my way at joe@meyerfire.com. Hope you find this helpful and that you have a great & safe week!

CodeCalls: A Quick Followup & Call for Action

4/16/2020

 
The past seven days have been a very exciting time with the launch of CodeCalls.org. If you missed last week's article, here's more about it.

This week's post is a quick one with an ask.

Feedback
In short, CodeCalls.org is a free database that brings together jurisdictions and designers to help clarify the parts of code that are not always written in ordinances. Jurisdictions can get what they need for operations while designers get a little more clarity and help in meeting local guidelines.

I've heard from many this past week about how they'd love to see this come together, and I greatly appreciate the input and encouragement. I've also heard a couple concerns that I'm optimistic we can incorporate as we learn and grow while working on this.

Viability
Our first goal is making sure the project is viable. Essentially we have to prove to ourselves that we will be able to provide enough valuable content that both designers and jurisdictions benefit. We're doing this by going all in on the State of Indiana. If we get things to work there, we feel comfortable that we can learn and expand into other areas.

I have a quick ask this week - if you have worked in Indiana, or know of people who do, could you put us in touch? My email is joe@meyerfire.com, my co-founder Chris' email is chris@codecalls.org, or if you got this post via email you can just reply directly to it. 

I'd love to have a quick conversation about how we can make the experience easy and that the benefits of helping will far outweigh the task of reaching out. I see that as the only way we can get this project rolling and I'd be thrilled to have that conversation. 

Thanks in advance, and have a great week!

Introducing CodeCalls.org: A Free Database

4/9/2020

 
Today is a very big day for me. I am finally launching the start of an idea I've had and brainstormed and discussed and revisited for a number of years now.

Finally. I could not be more excited about it.

Ever since the COVID-19 pandemic began impacting the world around us I've been pressed to rethink my own operations and what I'm contributing to the world. Articles, design content, PE Prep, and trying to find ways to help the knowledgebase of the fire protection community is good, but I started the website around the idea of impacting the community in a real and tangible way.

Today's new project is the start of what I hope could be a major positive impact for AHJs, designers, and installers.

What is it? A Code Call Database.

What is CodeCalls.org?
CodeCalls.org is a free website that is bringing together local jurisdictions, fire protection designers, engineers, and installers to clarify and collaborate local code requirements.

We're taking the areas of code in fire protection design that need local input, and helping jurisdictions get what they need to help first responders do their work.

​When we're done, we plan to have a searchable, filterable database where you can find local requirements based on a project's ZIP code, city or county name.
The Code Call Database

Where to Start? Indiana!
There tens of thousands of jurisdictions in the United States alone, how is all this data going to come together?

First, we're starting with our test case. If you work in the State of Indiana or have contacts who do, pay close attention today.

Our Goal is to gather jurisdictional requirements for 70% of Indiana's population by May 8th. That's in 30 days.
Picture
Why Indiana?
Indiana has a healthy mixture of urban, suburban and rural jurisdictions, so it presents a great test case to validate the concept. If we get enough momentum for Indiana, we feel confident in pursuing the project for larger coverage.

If we find that we can get enough momentum to clarify requirements for Indiana, then we feel that the project could be viable to expand to new areas beyond Indiana and beyond just the United States, too.

Why a 70% Coverage Goal?
In order for the database to work, the user experience has to be great. Both for jurisdictions and for designers & installers. We feel that if we can cover jurisdictions that account for at least 70% of the area's population, that we'll have enough data for a great user experience and a very helpful resource.

Is it Free?
Yes, the database will always be free for anyone to access. We're funding the development efforts as a joint project by MeyerFire.com and BuildingCode.Blog.

Why Should I Help?
If you're an engineer, designer or installer, why should you contribute?

For one - this is a way to clarify local requirements that will help in more fair and consistent bidding.

Second - we'll thank you by crediting your contribution with a link from the local listing directly to your company's website. If someone is looking for a local contractor or design outfit, they can search a ZIP code and immediately have contact information to you, the person who they know is already familiar with the local requirements.

If you're a jurisdiction, why should you contribute?

Simple - get your needs met. Are you tired of providing the same plan-review comments? Tired of answering the same basic questions in phone calls and emails? This platform is an easy way to clarify the gray areas of code and simply make your requirements more clear to those who are seeking them.

I Have Some Information for Some Areas in Indiana. How Can I Help?
You can contribute information for jurisdictions you're familiar with here. We'll thank you with a promotional link to your company's website and help get the information verified by the jurisdiction.​

See The New Site!
Click here or the link below to check out the new project. Let us know what you think by commenting or emailing me at joe@meyerfire.com. Would love to hear feedback on how we can make this helpful and accessible.
Picture
SEE THE CODE CALL PROJECT (CODECALLS.ORG)

The Two Drivers for Minimum Sprinkler Flow

3/25/2020

 
First - last week I put together a draft PDF cheatsheet for fire alarm design in elevators. Lots of great response to that tool. One major flub on my part - I didn't actually link to it. Here's an actual working hyperlink (fingers crossed).

K-Factor & Pressure Versus Area & Density
One of the hand calculations I do frequently when laying out sprinkler systems is comparing the k-factor, minimum pressures, and resulting flow for the sprinkler. It comes up all the time with residential-style, extended coverage, special application, and storage sprinklers.

Many hydraulic calculation programs do this comparison automatically. That being said, it is important to understand and compare the minimum flow from sprinklers for a hydraulic calculation.

Reducing unnecessary flow from a sprinkler reduces the total calculated flow from a system, which has major impacts on pipe sizing for some branch lines, cross mains, feed mains, and even the underground service size.

Driver #1: K-Factor and Minimum Pressure
There are two drivers for the actual minimum flow that must come from a fire sprinkler.

The first driver is the K-Factor and Minimum Pressure. This equation is
Q = k√P​

Read More

Fire Alarm Elevator Requirements (A Cheatsheet)

3/19/2020

 
Wow a lot has changed in a week. We're holding on fine here, but I hope you and your family are safe and healthy wherever you are.

Now back to more fun things like fire protection - 

After last week's debut of fire sprinkler requirements for elevators, I had a couple emailed requests for a fire alarm version. I love the idea and put some time into reviewing and organizing the requirements on the fire alarm side.

This first iteration is a draft, and if you're well versed in this arena I'd love for you to take a look and let me know what you think. Feel free to email me directly at joe@meyerfire.com, or comment on it here.

In the upcoming week I plan to incorporate ASME A17.1 and it's impact on the fire alarm side of accounting for elevators, hence the big [DRAFT] watermark on this PDF. 

Click on the image below to get a PDF copy of the Fire Alarm Elevator Cheatsheet:
Picture

If you know anyone that could benefit from this content, please consider forwarding them a link.

Hope you have a safe and healthy rest of your week! Thanks for reading.

When Are Sprinklers Required in Elevators?

3/12/2020

 
While it is a basic question, the code path is somewhat complex. When does an elevator require fire sprinkler protection?

Today I'm exploring the code requirements for elevator sprinkler protection under the International Building Code (IBC) and NFPA 13. Here's a free PDF cheatsheet for navigating these requirements. To download, just hover over the image and click print or export.

A special thanks to Philip Valdez who sent over the suggestion to put this one together. I hope you find it helpful! 

If you don't already get these free tools to your inbox, subscribe here. If you're having trouble viewing the image below, view it in your browser here.
DOWNLOAD ELEVATOR PDF CHEATSHEET
Picture
If you've found this helpful, consider sharing it with a friend or colleague. As always you can subscribe and get more free tools like this at www.meyerfire.com/subscribe. 

Thanks & have a great rest of your week!
<<Previous
Forward>>
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET THE TOOLKIT

    SUBSCRIBE

    Get Free Articles via Email:
    + Get calculators, tools, resources and articles
    + Get our PDF Flowchart for Canopy & Overhang Requirements instantly
    Picture
    + No spam
    ​+ Unsubscribe anytime
    I'm Interested In:

    AUTHOR

    Joe Meyer, PE, is a Fire Protection Engineer out of St. Louis, Missouri who writes & develops resources for Fire Protection Professionals. See bio here: About


    FILTERS

    All
    Announcements
    Book Review
    Calculators
    Career
    Course
    Design Challenge
    Fire Alarm
    Fire Events
    Fire Suppression
    Flammable & Combustible Liquids
    Flexible Drops
    Floor Control Valve
    Life Safety
    News
    NICET
    Passive Fire Protection
    PE Exam
    Products
    Site Updates
    Special Hazards
    Sprinkler Systems
    Standpipes
    Tools
    Videos


    ARCHIVES

    June 2023
    May 2023
    April 2023
    March 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    December 2020
    November 2020
    October 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    April 2018
    March 2018
    February 2018
    January 2018
    December 2017
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    May 2017
    April 2017
    September 2016
    August 2016
    July 2016
    June 2016
    July 2015
    June 2015
    May 2015

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2023 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • THE TOOLKIT
    • SUBMIT AN IDEA
    • BACKFLOW DATABASE*
    • CLEAN AGENT ESTIMATOR*
    • CLOUD CEILING CALCULATOR
    • DOMESTIC DEMAND*
    • FIRE FLOW CALCULATOR*
    • FIRE PUMP ANALYZER*
    • FIRE PUMP DATABASE*
    • FRICTION LOSS CALCULATOR
    • HANGER SPACER*
    • IBC TRANSLATOR*
    • K-FACTOR SELECTOR*
    • NFPA 13 EDITION TRANSLATOR ('19 ONLY)
    • NFPA 13 EDITION TRANSLATOR ('99-'22)*
    • LIQUIDS ANALYZER*
    • OBSTRUCTION CALCULATOR
    • OBSTRUCTIONS AGAINST WALL*
    • PLUMBING FIXTURE COUNTS
    • QUICK RESPONSE AREA REDUCTION
    • REMOTE AREA ANALYZER*
    • SPRINKLER DATABASE*
    • SPRINKLER FLOW*
    • SYSTEM ESTIMATOR*
    • TEST & DRAIN CALCULATOR
    • THRUST BLOCK CALCULATOR
    • TRAPEZE CALCULATOR
    • UNIT CONVERTER
    • VOLUME & COMPRESSOR CALCULATOR
    • WATER STORAGE*
    • WATER SUPPLY (US)
    • WATER SUPPLY (METRIC)
  • UNIVERSITY
    • JOIN
    • CATALOG
    • CONTENT LIBRARY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE Prep Series
    • PE 100-Day Marathon
  • LOGIN
  • PRICING
    • SOFTWARE & TRAINING
    • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT