This week I'm pulling back the curtain a little bit and showing a tool that is very much still under development. It's a water-storage tank sizer that incorporates a handful of decisions that go into water storage tank sizing. I'd like to get it in front of you this week as I'm looking for feedback on how to improve this tool. There's not a lot of great documentation on how to size water storage tanks, but there are plenty of variables that impact proper water storage tank sizing. With that said, check out the tool as part of our Toolkit package here: If you're in the water storage tank space and have tips or feedback, please email me at [email protected] or comment here. I'd be very much interested in ways to improve this one (or any tool for that matter). On a side note, this and many other recent tools are going to be included with a major MeyerFire Toolkit update here in the next few weeks. We've been working quite a bit on improving the activation/subscription process which has been no small task. When that gets cleaned up I'll be happy to send out the major update for the Toolkit. Hope you have a great rest of your week! Occasionally, as part of the upfront engineering work I do, I'm asked to identify the quantity and approximate size of clean agent storage tanks. The final calculations and actual clean agent system design is to be completed by a specialist at a later time, but my role is to make sure they have room allocated specifically to them early in the design process. As part of that effort in determining quantity and sizes of tanks, I'll estimate about how much agent the project will actually need. For that purpose, I've built the Clean Agent Quantity Estimator. It's built on NFPA 2001 and its' own agent weight formulas for FM-200 and NOVEC-1230. With a few parameters and assumptions you can very quickly get an estimate of the amount of clean agent your project would justify for a space. It's important to note here that these are estimates - actual agent weight will need to be fine-tuned once the pipe network has been laid out and sized. Do you see this tool being useful for what you do? What would make it better? Feel free to comment below here with ideas or feedback. Don't get these free tools? Subscribe here. Thanks & have a great week! Occasionally I come across projects where the contractor (my client) is looking to use listed anchors or attachments that are listed, but have various strengths associated with them. NFPA 13 lists the maximum spacing for hangers, but this maximum spacing doesn't always address these alternative hanging methods. NFPA 13 addresses these by requiring that any hanger assembly be able to support five times the weight of water filled pipe, plus 250 pounds. Based on this, I've created a calculator that reverses this process and calculates the maximum spacing for hangers depending upon the pipe size, type, and strength of a hanging element. As this is the first week out I only have I-P units (sorry international friends, I'll continue to work on this), but let me know what you think in the comments section below. Thanks and for those in the US have a great Thanksgiving week!
I was asked recently for a specific project how much flow the owner should anticipate coming from a building's main drain.
There are just a few factors that play into exactly how much water to expect. Is the drain serving as the main drain for a system? Is it only serving an inspector's test? Is the drain off a 1-inch pipe or 2-inch pipe? How much pressure is on the system? These are relatively easy to answer if you're familiar with the job, but each answer plays a role in determining how much water will come out of an open orifice. This week, I simplified a few of these parameters to create a quick inspector's test and drain calculator for fire sprinkler systems. This tool estimates the maximum amount of flow that could come from an inspector's test or main drain. It does not represent the actual amount of flow from a main drain or inspector's test. Read more about this challenge here. With it, you can estimate the amount of flow that will come from an inspector's test (use the k-factor option) or from a drain (diameter option), for the purposes of figuring out drain solutions from these outlets. βFor our international audience I have incorporated real units from the get-go this time. It's a free tool that's now live on the site, here. Give it a spin and let me know what you think in the comments here. β Know others that might find this helpful? Send them a link or tell them to subscribe here. Thanks & have a great week! Over a year ago I released a Thrust Block Calculator online.
It that takes a small handful of inputs and offers sizing and dimensions according to NFPA 13. The tool has been a reasonable hit except for one repeated request from the field – the thrust block weight. Until now designers and engineers using the tool still had to convert the minimum required volume into the minimum weight based on the density of the concrete. Hand calc no longer! Special thanks to Sinisa who offered the reminder after I asked for pet peeves or upgrade requests in last week’s post. If you’ve never used the tool and would like to check it out, here’s the link to it. It's free and available now. Last item for this week - I'm circling back to a call for water storage tank experts. If you're experienced in this space and would like to review a new tool I'm working on, please shoot me an email at [email protected]. Would be happy to set up beta testing. Thanks and I hope you have a great rest of your week! If you know someone taking the PE Exam this week, it's time to give them a hug. Maybe not an actual hug; don't be a creeper, but maybe a kind supportive attaboy wouldn't be a bad idea.
Final Call for the PE Exam This Friday is the day for the 2019 Fire Protection PE Exam... the same exam that at least two hundred fire protection professionals have been honing in on the past few months. Changes Coming This year marks the last year of the written examination. Major changes are on the horizon for the Fire Protection PE in 2020, including question style, references, and going to a computer-based environment. The biggest change may be that no longer will any resource be allowed in the exam room. There'll be plenty to cover on the 2020 exam later on. Perhaps because of the big looming changes, we've seen a major uptick around here in the interest in the Fire Protection PE Exam. I would guess that this year will set the record for the number of examinees. That's a great thing. I'm thrilled that the fire protection industry as a whole is growing, and I hear almost weekly about how rare Fire Protection Engineers are in our industry. What is the PE Exam? For those who don't know, the PE Exam is the Principles and Practice of Engineering examination which is administered by the National Council of Examiners for Engineering and Surveying (NCEES). The exam is the major milestone to getting a license to practice as a Professional Engineer in the United States. In order to take the PE Exam, examinees must typically first complete a four-year ABET accredited engineering program and a Fundamentals of Engineering (FE) Exam as well as accruing four years of experience working with a licensed engineer. Of course the requirements vary by state but that is the most common requirement. Last Minute Exam Advice If you have a copy of the Prep Guide you already know there's quite a bit of detail on exam advice passed down through the years included in the book. Regardless of how many hours you've spent studying (whether two or two hundred), there will always be topics that are over-emphasized, poorly worded questions, and niche questions that seem to have no basis in any reference materials. Keep calm and exam on! Skip and come back to questions later. Some of these questions are just on trial for future exams and others will get disputed and thrown out. All you can do is your best. Don't worry about surprises you can't control but focus on what you know and give it your best effort. Best of luck, you've got this! Updates for 2020 PE Exam If you have sent in information on the 2019 Edition for suggestions or potential updates, thank you! With all that's happened around here this summer I haven't been as responsive to PE Exam emails as I've tried to be in the past. Please know that I go through all of these and make updates for future examinees, and I greatly appreciate your time in sending suggestions in. New Feature on Quick-Response Remote Area Reduction I've had a pet peeve about one of my own tools. Awhile back I created a calculator that will determine the allowable reduction in the hydraulically remote area based on the use of quick response sprinklers. It's a quick-hitter and one I use often. Each time I use it, though, I still end up using the reduced area and punching in 1.2 times the square root of the new area in order to lay out my hydraulically remote area. Being that I'm all about convenience (ie: laziness) and efficiency, I've now added that basic calculation in the tool as well. You can see the new feature here. If you have similar nuances on how these tools can be improved, let me know! I'm always happy to entertain new ideas. You can always reach me at [email protected]. Have a great week! Sometimes the best inspiration for new tools on this site come from basic frustrations with repeated tasks. The past few weeks I’ve finally come to the point where I needed to scratch an itch – plumbing fixture counts. What does this have to do for code & life safety? It doesn’t – other than (generally speaking) code summaries will often address plumbing fixture count minimums as part of the overall building code evaluation. Here’s my scratched itch – a calculator that will populate minimum requirements for plumbing fixture counts based on the 2018 International Building Code & 2018 International Plumbing Code. Now, with only four inputs you can quickly grab the minimum fixture counts from the 2018 IBC. It’s more than likely that something already exists in the vast spans of the internet for this, but in the meantime at least I know we all can stop wringing the calculator for a few basic number crunches. If you’re already a Toolkit user, you can download this update and use it right away on the downloads page here: www.meyerfire.com/downloads If you’re not already a Toolkit user, why not? Join in on all the expanded tools we have by getting the Toolkit here. Is this something you’d use? If you’d find this useful and would like to see it expanded to other editions of the IBC (or other standards), let me know by commenting here. I’d be happy to break this out for prior IBC editions if it’s something that’d be beneficial.
Following the interest and popularity of the ceiling-mounted obstructions tool, I've been working on some new tools that cover other obstruction situations which we often encounter. This week's post is a quick demo of the progress for one of these obstruction situations, which is the soffit against a wall condition.
One way NFPA 13 addresses soffits is by shifting a sprinkler away from the wall, which allows water from the sprinkler to throw below the soffit. With only two input values this tool will quickly determine the horizontal distance a sprinkler needs to be located away from a soffit in order to meet NFPA 13 Figure 8.6.5.1.2(b) (2016 Edition). Give this demo tool a quick try and comment below with any concepts you'd like to see added to this tool or the site. Thanks in advance! β When I was six years old, I came home from school unexpectedly excited one day. I ran up our driveway, pushed wide the door and yelled to my mom. “You won’t believe it! There’s this place at school where you can go through shelves and shelves of books and pick out anyone you want – and it’s free! They call it a library.” It wasn’t one of my mom’s proudest parenting moments, but in our house, we never pretended to be great readers… or apparently even pretended to introduce kids to a library. I guess I’ll just come out and say it… Both of my parents are accountants. Now, I know what you’re thinking, and yes, the accountants are where my well-rounded sense of humor comes from. But there’s another big benefit to having parents as accountants – and it’s having a love for spreadsheets. I’m not sure if little excel formulas naturally run through my veins or whether it was every family calendar my parents ever created, but one way or another I thoroughly appreciate the power a spreadsheet has. Even if your parents are not both CPAs, there’s a place for Microsoft Excel in your engineering life. Excel isn't just made for your uncle accountant anymore - there's potential any engineer can love. For one, Microsoft Excel is not called the “Swiss Army Knife of Software” for naught. Excel is a blank canvas for any calculation you need to make. You can quickly create and repeat repetitive calculations to speed up and organize your workflow. You can complete reports, forms, create charts, tables, organize content, or use any of a myriad of highly powerful tools. Here are a few of my most often used formulas:
That’s pretty much all of my secret sauce. About 95% of the tools created combine those formulas alongside mathematical operators (like max(), min(), sin(), sqrt(), etc.). One of the best parts about using Excel is that you may already have access to it. If your company has a Microsoft Office suite (or what’s now their subscription model with Office 365), you already have access to these tools. Creating helpful resources is what we’re all about, and Excel is the epitome of giving you, the rockstar designer or engineer, the ability to create and flourish with the tools you need. You didn’t get into the industry to do poor, sloppy work. You came here to help save lives. We shouldn’t have to wait for programmers to create the daily tools we need to do great work. Excel is one way you can organize and validate the great work you do. There came a point near the end of my undergraduate work and at the beginning of graduate school where I realized I needed to create a clean, organized method to show details within calculations. The method I slowly developed needed a single logic path, had to be easy to follow, would thoroughly explain the process, and had to allow the easy repetition of the work. What’s resulted is the standard format that’s used in the PE Prep Guide and on many of the tools you’ll see around this site. Concepts are researched, painstakingly created, tested, refined, tested, refined, beta tested, and refined more. Standard formatting for MeyerFire tools - note the equations and worked examples with references cited. If you’ve followed the blog for a while, you already know the blog, daily forum, and even the PE prep materials are all created to help foster discussion that leads to shared expertise and knowledge. Outside of a few major players and organizations, the fire protection industry is comprised of thousands of thousands of small outfits that welcome this shared expertise. Our industry thrives on the contributions from a wide spread of individual parties. Don’t let me or anyone else douse your enthusiasm to create resources that improve your ability to impact the industry. Keep on keepin’ on. Oh and remember to take your kids to the library.
Looking for an opportunity to turn a basic concept into a controversial one on a project? Great! This week I'm exploring the quick-response remote area reduction that's provided in NFPA 13.
Suppress Early, Suppress Less The concept behind reducing the calculated hydraulically remote area in a fire sprinkler system is entirely based on fighting a smaller fire earlier in the development of the fire. There's a handful of factors that contribute to the timing of sprinkler response (a good future discussion), which include the thermal sensitivity, sprinkler temperature rating, distance of sprinklers relative to the ceiling, sprinkler spacing, ceiling height, and dynamics of the fire itself. The reduction in the hydraulically remote area is based upon comparative tests of quick-response against standard-response spray sprinklers. According to the NFPA 13 handbook, the tests demonstrated that the earlier the water is applied to the fire, the smaller the fire and ultimately the less number of sprinklers needed to activate. Not Universally Accepted While the remote area reduction has been included in NFPA 13 for years, it's not universally accepted. Many engineer specifications don't allow the reduction, and design standards for major organizations such as the Department of Defense (UFC 3-600-01) don't permit it either. Why not accept the remote area reduction, if NFPA 13 includes it? Like other elements in hydraulic design for fire sprinkler systems, not using the remote area reduction provides an additional safety factor to the system. Additionally, since the quantity of sprinklers relates to the quantity of water flowing in the system, main sizes are directly impacted by using or not using the quick response area reduction. Building owners may opt to not want to reduce the remote area to preserve reasonable (larger) main sizes and give themselves flexibility on building modifications and sprinkler system changes in the future. Quick-Response Area Reduction Calculator This quick calculator is in part a checklist of prerequisites to reduce the remote area on a fire sprinkler system, in part a method of showing your work, and in part a quick calculator on determining your final remote area size. Don't see it below? Give it a try here. β This site is all about helping you shine in fire protection. Want these weekly tools & articles? Subscribe here, for free. |