It is a popular and well-established concept that water and electricity don’t mix. Water is electrically conductive which creates a major hazard of electrocution where a continuous pool of water meets a live electrical feed. Can We Omit Sprinklers in Electrical Rooms? On a few occasions I have come across building authorities and building owners who assume that sprinklers will not be installed inside traditional electrical rooms. Why? The basic tenant that water and electricity don’t mix. While the concept is important, the intent of sprinkler protection throughout a building is not just for each item within a building, but the building itself. The primary intent of sprinklers is suppression – or stated differently – to prevent the growth of fire from the room of origin throughout a building. This includes all the rooms and spaces beyond just the electrical room where a fire could begin. This week I’m digging into guidance surrounding electrical rooms. NFPA 13 Guidance
NFPA 13 (2002 Section 8.14.10.3, 2007-10 8.15.10.3, 2013 8.15.11.3, 2016 8.15.11.2, 2019 9.2.6) allows sprinklers to be omitted in electrical rooms, but only where each of the following are met:
Concerns with Providing Sprinklers in Electrical Rooms Providing sprinklers within electrical rooms could:
Historical Approach Prior to the 1994 edition of NFPA 13, important electrical equipment were required to have hoods (or shields) comprised of non-combustible construction to prevent direct contact by sprinkler discharge. All electrical rooms were required to be sprinkler protected. Beginning with the 1994 edition, NFPA 13 introduced language to address concerns for firefighter safety and equipment damage. Sprinklers could be omitted in electrical rooms where the room contains dry-type equipment (no oils), is dedicated to electrical equipment only, is fire-resistant to reduce fire spread, and the room has no storage hazard. The 2016 Edition, the requirement for equipment hoods or shields was removed to direct it under the scope of NFPA 70. Just recently for the 2019 Edition new text was introduced such that no storage is permitted (non-combustible storage had been allowed) and liquid-type K-class (less flammable, non-spreading fluids) would be allowed. International Building Code Input The International Building Code (IBC) does not allow the omission of sprinklers “merely because it is damp, of fire-resistance-rated construction, or contains electrical equipment” (IBC 2000-18 9.3.1.1.1). Within the same code section, the IBC does allow sprinklers to be omitted in “generator and transformer rooms separated from the remainder of the building by walls and floor/ceiling or roof/ceiling assemblies having a fire-resistance rating of not less than 2 hours.” These rooms must have an approved automatic fire detection system. According to IBC commentary, buildings with sprinklers omitted in one of the sections allowed by the IBC would still be considered fully-sprinklered throughout and in compliance with the code and NFPA 13. This distinction is important as it carries eligibility for code alternatives, exceptions and reductions. Today’s Consensus Combined, both the IBC and NFPA 13 require electrical rooms to be protected unless the prescriptive alternative option is followed. As NFPA 13 commentary outlines, sprinkler systems have been successfully installed in rooms containing electrical equipment for over 100 years with no documented instances of a problem. While still seemingly controversial, most projects designed today include sprinkler-protected electrical rooms. Get More If you enjoy these articles, subscribe here. If you're already a subscriber, consider forwarding to a colleague. MeyerFire is all about dissecting real challenges that real people face in fire protection design. I'm thrilled you're a part of our journey for better fire protection worldwide.
Mike
7/18/2019 08:31:40 am
Great synopsis Joe,
Derrick Shaver
7/20/2019 08:23:56 am
Since most clients don't want water in their IT server rooms, wouldn't a clean agent be more effective in this situation?
Ben O'Regan
7/21/2019 02:55:55 am
The companies that sell clean agent systems have done a great job convincing people that clean agent is ideal for computer server rooms. The reason for upselling customers on clean agent systems is very simple - that's where the big contractors make their money. The market for sprinklers is very competitive with so many little contractors competing with the big ones, but clean agent systems always have a healthy profit margin.
Derrick
7/21/2019 10:15:10 am
Wow...thanks Ben...very good information
Ben O'Regan
7/22/2019 03:19:55 am
You are very welcome Derrick. I think it's good to have discussions like this online.
JOE MEYER
7/22/2019 07:38:53 am
Ben,
JOE MEYER
7/22/2019 07:33:12 am
Just to be clear, this article isn't addressing server rooms with alternative protection, but rather just basic electrical rooms.
Ben O'Regan
7/22/2019 08:39:30 am
Hi Joe, Great Blog!!
JOE MEYER
7/22/2019 08:42:33 am
Yes, you nailed it. Well said!
Scot Deal
7/26/2019 06:18:48 am
I am a bit confused as to why we hesistate to install wet-pipe sprinklers to protect electrical or computer rooms.... put another way... what part did we not understand about the above article where it wrote
Doug White
7/24/2019 05:52:51 pm
Joe,
Ben O'Regan
7/25/2019 12:29:24 am
Hi Doug,
Jeff Yuill
1/8/2020 10:47:56 am
I would suggest that most electrical rooms do not have enough combustible loading within to set a sprinkler head off in the event of a fire involving the cable coating (XLPE) or some other combustible compoenent of the switchgear.
James
1/8/2020 02:14:29 pm
Jeff - if we're talking a smoldering fire with a cable or series of cables - sure. Those won't activate a sprinkler in any type of room until it grows large enough that the ceiling temperature is 150+ deg F. Comments are closed.
|
ALL-ACCESSSUBSCRIBEGet Free Articles via Email:
+ Get calculators, tools, resources and articles
+ Get our PDF Flowchart for Canopy & Overhang Requirements instantly + No spam
+ Unsubscribe anytime AUTHORJoe Meyer, PE, is a Fire Protection Engineer out of St. Louis, Missouri who writes & develops resources for Fire Protection Professionals. See bio here: About FILTERS
All
ARCHIVES
April 2024
|